What does the NEC say, if anything, about...

What does the NEC say, if anything, about...

What does the NEC say, if anything, about...

(OP)
...cable (both 5kV and 480V) exiting cable tray.  Note the cable is not armored cable.  Let us say that cable is exiting the cable tray...travelling some distance...then terminating at the pecker-head.  Is there some maximum distance this cable can travel before it needs to be protected by flex (sealtite) or rigid conduit?  Looking for something in "black-and-white" if at all possible.  Thanks in advance!  

I attempted to attach a couple photos of instances that spawned such a question; however, it timed out.  The photos are small (60-70k).

RE: What does the NEC say, if anything, about...

Maximum distance is zero per NEC, unless the cable is listed for being run unprotected.  See Article 336 in NEC.  

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources