Flag pole design
Flag pole design
Flag pole design
I need to design a flag pole (wind pressure of 20 psf, 5" dia pipe, 21' tall). How do I proceed? What are the design steps? I would appreciate your help.
RE: Flag pole design
There are embedded pole equations in the IBC for Flagpole foundations.  If you have a slab at the ground level it is considered constrained, if not, use the unconstrained equation, equations 18-1, 18-2 and 18-3 in Chapter 18.  The pole itself is a cantilever, M=wl^2 / 2, check against allowable stresses for steel...
StructTaco, per equation 18-1, P is applied lateral force in pounds. How do I calculate P? Also, please note that I have a cloth flag (4'x4') at the top of the pole. Is this P the resultant of lateral forces on flag (if we need to consider it) and on pole itself because of its diameter (5" diameter in this case)?
You need the NAAMM Flagpole Manual, and Guide Specifications For Design of Metal Flagpoles, which cover this exact thing, including wind effects from the flag.
http://www.naamm.org/items.aspx