If a Feeder ckt supplies only 3-ph and 208 1-ph loads, will adding the neutral conductor minimize voltage imbalance ? Or does neutral accomplish nothing ?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Neutral to minimize voltage imbalance
|
Neutral to minimize voltage imbalanceNeutral to minimize voltage imbalance(OP)
If a Feeder ckt supplies only 3-ph and 208 1-ph loads, will adding the neutral conductor minimize voltage imbalance ? Or does neutral accomplish nothing ?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Neutral to minimize voltage imbalance
RE: Neutral to minimize voltage imbalance
RE: Neutral to minimize voltage imbalance
There are cases where connecting the neutral will solve voltage inbalance, but this is because a ground fault exists that will be revealed (in a bad way) when you connect the neutral to ground.
RE: Neutral to minimize voltage imbalance
For instance let's take a building of 3 dwelling units. Let's say apartment A load is 1000 w at 208 V. Phase A to neutral resistance is then ResA=208^2/1000=43.26 ohm.
Let's say apartment B load is 100 w and Phase B to neutral resistance will be ResB=208^2/100=432.64 ohm.
Now, let's say no load for apartment C. If no neutral is provided-that means the neutral is disconnected at the common building supply cable- then from live A to live B will be 208*sqrt(3)=360 V.[See the sketch]
The common current flowing from A to B=360/ (432.64+43.264) =0.75646 A.
Then the A load will get 0.75646*43.26=32.72 V and the load B 0.75646*432.64=327.27 V.
If a neutral continuous conductor is provided the voltage will be equilibrated and the each individual current will flow back to the source [transformer].
RE: Neutral to minimize voltage imbalance
I believe that you misunderstood the OP. The system is 208V Ø-Ø (208/120Y - common in USA) and there are no loads connected Ø-N.
I agree with others that there is no need for a neutral conductor. There is a need for an equipment grounding conductor to ensure tripping for ground faults.