Grounding Requirements

Grounding Requirements

Grounding Requirements

(OP)
All,

I have a 53 foot x 38 foot structure that will house very large 66" water pipes.  This structure otherwise known as a valve pit will be an area to house electrically motorized operated valves.  The structure will not require piles for its foundations but will have spread footings.  There will be a lot of rebar and concrete.

My question is does this structure require grounding?  If so what is the governing code that dictates that this structure shall be grounded?

These massive pipes will have electrically operated valves that will have the feeder cable grounded.

I have read NEC Art 250.32 Bldgs or structures supplied by a feeder(s) or branch circuit(s).

I believe that this article in the NEC tells me that this structure that I have described DOES require a grounding electrode.  Please provide input as to whether or not my thinking is in line with this code reference.


Should I have a ground loop of 4/0 AWG bare cable around the valve pit structure with a few driven ground rods and periodically attaching to the rebar with grounding electrode?

Thanks in advance.

RE: Grounding Requirements

A grounding electrode is required unless it's supplied by a single branch circuit. See exception under 250.32(A). The NEC does not require a 4/0 loop however. Read the sections about allowable grounding electrodes.

Alan
----
"It's always fun to do the impossible." - Walt Disney

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources