Composite Beam Deflection
The commentary in AISC 13th states that for realistic deflection calculations Ieff should be taken as 0.75*Iequiv.  Does this mean multiply Ieff as calculated per Eq. C-I3-3 by 0.75?  Does Iequiv = Ieff?  Reference pages 16.1-308 to 16.1-309.  There is also an option to apply the 0.75 factor in RAM Structural System v14.
Thanks.
RE: Composite Beam Deflection
Ieff = 0.75Iequiv where Iequiv is calculated per C-I3-3.  In the first edition of the manual equation C-I3-3 was incorrectly labeled as Ieff.