Application of VLF test set,Allen Bradley says to connect the ground lead from the hi-pot tester to the load side of the contactor. What technical reason would there be for doing this.

Thanks
Mike Boudreau

RE: Vacuum bottles

If your testing a vacuum bottle with a VLF test set (or any other single point output tester AC, DC or VLF) the output lead (hot lead) would be placed on one side (in your case LINE side) of the bottle.  The return lead (or ground lead) is placed on the other end of the bottle (load side).  This will test the bottle its self, just remember to test the primary insulation components at the proper level required for your application.  I am not aware of the test specifications or acceptable criteria for VLF testing of switchgear.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources