Conductors Considered Outside the building

Conductors Considered Outside the building

Conductors Considered Outside the building

(OP)
It is my understanding that in order for conductors or cables to be considered outside a high rise building NEC 230.6 shall be applied for the installation of the vertical raceways encased in concrete not less than 2 inches thick. Can anyone tell me what type of conduits are allowed to be installed in the vertical raceways and how are they to be supported ? Please reference the NEC CODES that appropriately provide an answers to the latter questions...  Thank you in advance    

RE: Conductors Considered Outside the building

The type of conduit is not specified, so any type of conduit that is otherwise allowed by the NEC would be permitted. It would need to be a type that is allowed to be encased in concrete.

Alan
----
"It's always fun to do the impossible." - Walt Disney

RE: Conductors Considered Outside the building

(OP)
Alehman,

"so any type of conduit that is otherwise allowed by the NEC would be permitted" Please explain THE FOLLOWING  " otherwise allowed by the NEC" allowed where?  

RE: Conductors Considered Outside the building

In other words the conduit type would have to be allowed for your application were it not encased in concrete.

For example, the NEC wouldn't allow ENT for a medium-voltage feeder so you can't use it for your application encased in concrete.

Alan
----
"It's always fun to do the impossible." - Walt Disney

RE: Conductors Considered Outside the building

If the run is long, you may have an issue installing the conductor supports that are required by 300.19 and still keep the conductors "outside of the building".

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources