Generator Neutral Grounding Resistance Sizing
Generator Neutral Grounding Resistance Sizing
(OP)
I have a generator 3000 kVA, 400 V, 50 Hz that requires a neutral grounding resistance for short circuit protection.
How can i size that resistor in detailed steps?
How can i size that resistor in detailed steps?






RE: Generator Neutral Grounding Resistance Sizing
For the start.
thread238-250961: IEEE-142-2007 Grounding of Industrial Systems
h
I would recommned to you search on the Forum too, lot of topics on the issue.
Good Luck.
Slava
RE: Generator Neutral Grounding Resistance Sizing
RE: Generator Neutral Grounding Resistance Sizing
Step two: Multiply the voltage by the desired maximum ground fault amps. This will give you the watts that will be dissipated by the resistor under worst case conditions.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Generator Neutral Grounding Resistance Sizing
Alan
RE: Generator Neutral Grounding Resistance Sizing