Flex head pipe again
So educate me on this minimum bend stuff??? as found on page 5
http://www.flexhead.com/pdf/submittalpackage.pdf
http://www.flexhead.com/pdf/Commercial- ... -Guide.pdf
so is there a maximum bend ??? according to manufacture the answer is no!!
"""Q: Do putting additional bends in the product greatly affect my friction loss calculations?
A: No. The published friction loss data is a worst case head loss calculation. Each hose was tested with the maximum amount of bends physically possible bent to the minimum bend radius top create a worst case head loss calculation. """"
RE: Flex head pipe again
and still do not understand the 3 inch minimum???
fm allows 7 inch minimum bend????
not very clear what is right and what is wrong????
The minimum bend is simply the minimum radius allowed for the bend. It is 3" for UL and 7" for FM.
Think of a typical gooseneck (return bend) for a hard piped system. You have a 4" nipple up, a 6" nipple over and then a drop nipple. With hard pipe, you could get a close nipple in there and have the center to center dimension between the elbows of about 3-3½".
With a flex head, the minimum bend is 3" using UL listed criteria. Therefore, the up and down portion of a typical return bend can be no closer than 6" center to center. With FM criteria, they would have to be 14" apart.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
if you look at page 5 the picture to the right on the bottom, if you bend that pipe more is it legal????
if there is any bend in the pipe as long as it is three inches or more it is good to go.