Heating of Ferromagnetic Material surrounding HV Cable
I am aware that when a single phase cable is enclosed by a ring of ferromagnetic material that it can heat up and cause damage to insulation. This I have learnt from previous posts.
My problem is that I need to justify this in a report to my client.
We have a HV Cable 132kV with an earthed screen running through a steel support structure. The structure has four vertical posts (parallel to current direction) and cross members the whole structure is bolted together without an insulating plate or anything.
Can anyone point me in the direction of the physics behind the heating?
I would ideally like to run a calculation on paper to find the circulating current under fault conditions.
Thanks in advance for your help,
Andrew
Andrew
RE: Heating of Ferromagnetic Material surrounding HV Cable
This is a load current problem, not a fault current problem, so I'm not clear what you are asking regarding "circulating" current.
Thanks for the reply.
I am familiar with the situation of a steel conduit.
In this situation, I have steelwork that is surrounding the cable. I am told that under normal load, the steelwork may heat up.
Under fault conditions some sparks could be expected at the bolted connections.
I have drawn a quick sketch to try and make the situation a bit clearer. Hope it clarifies things.
The blue lines represent galvanized steel with a right angle cross section.
The red represents the cable.
Andrew
Can you confirm whether this is a single or three phase installation?
The Cable passing through the steel loop is single phase,
The system is 50Hz AC to clarify also.
David,
I agree that the steel structure surrounding the cable is like the Core of a CT. However, my understanding was that the core of a ct is then wrapped in copper coils. The flux linkage between the main conductor (primary) and the copper coil on the CT (Secondary cause a current to flow. The math for this is Ok. For this reason I see finding the current in the steel structure subtly different to the ct.
In this case, I only have the steel bar. I am concerned about eddy currents in the structure and also what happens under fault conditions.
Example 1, if I were to use a solid steel plate and pass a single phase conductor through a hole in the plate, you would expect the plat to heat up if the load current was high enough. What direction would the current be flowing in to cause the heating?
Example 2, I am told that during testing under fault conditions, the high currents in the steel work cause sparks to fly at the bolted connections between the cross members. This is apparently due to the high resistance galvanizing between the two steel members. What direction is current flowing? How do I work the magnitude?
I currently know that the magnetic field in the vicinity of the cable will be a circular field around the cable with magnitude.
B = uI / 2*Pi*r
The circular field will induce a current in the loops on the side view because the B field is cutting the vertical steel members in the same direction.
A changing magnetic field here will give a changing flux and therefore EMF in the loops on the side. This is classical mutual induction.
What I dont understand is where any current can come from a closed loop at 90 degrees to the direction of current flow.
Im trying as hard as I can to state the problem clearly.
Thanks for your help,
Andrew
The steel forms the core and the conductor of the 1:1 CT. An actual CT has a laminated core to prevent or greatly mitigate current flowing in the steel core.
Bill
"Why not the best?"
Jimmy Carter
The problem –as I suppose-was the phase-to-ground short-circuit heated the iron close loop mainly at connection point.
The posts were hanged between ceiling and floor by mean of bronze inserts and the racks were cast aluminum made.
By the way, using bronze bolts instead of steel it poses another problem since the bronze screw is not so resistant as steel and the thermal extension or retraction force in the iron structure may break the bronze screw down.
Eddy currents will be formed around this circular field.
The current density in the object will be the main variable dictating heat dissipation.
Current Density seems to be higher at the corners and connecting pieces.
I suspect to get a good quantitative answer I'll need some 3D simulation going on.
Thanks for the help!
Andrew
http://forums.mikeholt.com/showthread.php?t=119373
Ghost
If we neglect the hysteresis losses and we'll take only eddy current losses the usual formula is:
[see -for instance:
http
Pe=(pi()*B*t*f)^2/(6*10^7*d*ro) w/kg
where flux density (B) is in Gauss, frequency (f) in Hz, laminate thickness (t) in cm, density (d) in g/cm3, and electrical resistivity (ρ) in μΩ-cm.
If the "laminate" thickness will be 5 mm and the iron properties:
d=7.8 g/cm^3; ρ=0.1 ohm.mm^2/m=10 μΩ-cm; miufe=2000 relative permiability what we need is B.
Let's say cross members will be arranged in a square 0.5*0.5 m. The periphery length is then 2 m.
If will be a non-magnetic gap in this periphery of lengap [m] length, the "magnetic circulation" will be:
Sum(H*L)=Sum(I) that means:
Hfe*(lengfe-lengap)+Hgap*lengap=I[A] where Hfe and Hgap are the magnetic field intensity.
Hfe=B/miuo/miufe ; Hgap=B/miuo.
B/miuo/miufe*(lengfe-lengap)+B/miuo*lengap=I[A]
B=I[A]*miuo/[(lengfe-lengap)/miufe+lengap] Wb/m^2
miuo=4*pi()/10^7 H/m vacuum permiability
If lengap=10 mm[0.01m] then B=0.114 Wb/m^2 =1143 Gs and then Pe=((pi()*1143*0.5**50)^2/(6*10^7*7.8*10)=1.7w/kg
the weight of a iron square could be 0.5*5*7.8*200=3900 g=3.9kg
The total losses with gap=3.9*1.7=6.63 w
If lengap=0 then B=1.25 Wb/m^2 and Pe=208 w/kg
The total losses without gap=3.9*208=811 w and in free-air of 30 oC the iron temperature is 100-120 oC.
If the current will be 1700 A B=2.1 [saturated state] total Pe=2340 w and the iron temperature may be
300 oC.
You said you have a single phase cable with a grounded shield. If so, I would think this shield would not allow the field to cause a problem. Maybe some one else could confirm this concept.
Shields are really all about capacitive shielding not inductive shielding. These heating effects are caused by inductive coupling.
Keith Cress
Thanks for the post! Thats a very similar situation to what I have.
7anoter,
Whoa! Thats the sort of detail I needed. I havent fully tried the application myself but I'll spend some time trying it out. Thansks. (Star for you!)
Wareagle,
itsmoked is quite right. The effects I am concerned about are from inductive coupling, I.e Electromagnetic induction. The magnetic field will permeate the shield.
Thanks again.
I'll post up the solution once I have applied it to my particular situation.
It is only the steel or iron between conductors that is the problem. not around all three. Maybe easier to change the steel to stainless or cut it out and design a structural retrofit.
Then for "no-gap" and 1000 A the iron temperature [cooled in natural ventilation of 30oC air] will be 300 oC. and for 1700 A [through 132 cable] will be 700oC.