We are using a step up transformer feeding power from Generator ( 480V Delta/4160V Wye). At 480V level, a load bank is connected. I wonder if we could use this transformer as a step down transformer( Wye4160V/480V Delta). The power would be from Utility. The generator would  be disconnected. The problem is, how  will the load bank  be connected to Delta System.  

RE: Step up Transformer to Step down Transformer

If the transformer does not have unidirectional on-load tap changer gear, then there should be no problem backfeeding the trafo.

I don't understand your load bank Delta problem. It's already working from a delta connected generator, doesn't it ?

Muthu
www.edison.co.in

RE: Step up Transformer to Step down Transformer

Why would you even need a load bank if you ditch the generator?

Keith Cress
kcress - http://www.flaminsystems.com

RE: Step up Transformer to Step down Transformer

I read this twice.  You're going to load test the utility?

old field guy

RE: Step up Transformer to Step down Transformer

Utilities like for customers to load test them.

RE: Step up Transformer to Step down Transformer

(OP)
4160V system will be connected to a new generator, which will need to be loaded before the other loads are connected.  

RE: Step up Transformer to Step down Transformer

When you use transformer backwards you need to make sure that your tap settings are at normal otherwise your core losses will be high and transformer will run hot based on tap settings.

RE: Step up Transformer to Step down Transformer

Define "backwards".  There is no "right" direction through a transformer, therefore there can be no "wrong" or "backward" direction.

RE: Step up Transformer to Step down Transformer

I would take backwards to mean the reverse of a stepdown. It's not important in the way the transformer operates, but it is important in calculating the voltage effect of the taps on the transformer.

Both are correct in that there is no backwards, and there is a forwards.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources