Step up Transformer to Step down Transformer
Step up Transformer to Step down Transformer
(OP)
We are using a step up transformer feeding power from Generator ( 480V Delta/4160V Wye). At 480V level, a load bank is connected. I wonder if we could use this transformer as a step down transformer( Wye4160V/480V Delta). The power would be from Utility. The generator would be disconnected. The problem is, how will the load bank be connected to Delta System.






RE: Step up Transformer to Step down Transformer
I don't understand your load bank Delta problem. It's already working from a delta connected generator, doesn't it ?
Muthu
www.edison.co.in
RE: Step up Transformer to Step down Transformer
Keith Cress
kcress - http://www.flaminsystems.com
RE: Step up Transformer to Step down Transformer
old field guy
RE: Step up Transformer to Step down Transformer
RE: Step up Transformer to Step down Transformer
RE: Step up Transformer to Step down Transformer
RE: Step up Transformer to Step down Transformer
RE: Step up Transformer to Step down Transformer
Both are correct in that there is no backwards, and there is a forwards.