Hi,

We have been ask to test the ground grid of an existing petrochemical plant.

The plant have 2 exterior substations, and a lot of interior substation.

The exterior substations are interconnected with a lot of thing, like building, and it's nearly impossible to isolate their ground grid.  Also, there's a railroad close to the substations that will probably affect the result.

We read that in this situation, the touch potential measurement is a good solution.  See the last section of the document:  
http://www.dranetz-bmi.com/pdf/groundprinciples.pdf


So, we would like to do this test for the 2 exteriors substations, and do a continuity test of the ground conductor for all the interior substations.

Is there any other and better option that we can do.  The client doesn't really have an idea of what he want to be tested, it's more like a demand of his insurance company for safety.  We would like to do the best we can to insure personal safety, without exorbiting cost.

Thanks for your help

 

 

RE: Testing ground resistance of interconnected ground grid

Read the answer to my question on this thread, but I think this would be too expensive.
STEP AND TOUCH POTENTIAL TESTS ON LARGE SYSTEMS.
If I were you I would measure the ground resistance at major locations and ignore the interconnection whose contribution is small.This would indicate any problem areas. IEEE 665 does not recommend connecting the switchyard grid to a power plant grid if more than 200 m apart.This standard although for power plants, has some good guidlines, including rail roads tracks.     

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources