How accurate are digital meggers ?
Today, I had the uneasy experience of meggering a generator rotor winding (same temperature, time span of 10 minutes, same voltage of 500 V) with 3 different digital meggers (Two Fluke USA and one Kyoritsu Japan)and getting 3 widely differing values of about 600 megohms, 1500 megohms and 5000 megohms.
Is the case of no two clocks show the same time ? Is it time then to go back to the old & trusty hand-cranked analog meggers ?
Muthu
www.edison.co.in
RE: How accurate are digital meggers ?
And to think I sunk a few thousand dollars for these "brand" names... sheesh...
Muthu
www.edison.co.in
These things should be checked for calibration.  NETA says annual calibration checks.  If you're concerned, you can whip up an impromptu "standard" for a few bucks and an hour's time with a few resistors and hardware purchased off the internet.  It won't be an "official, traceable to NIST or whatever" standard, but it will let you do a reality check on your test equipment.
Check the resistance function at a few points.  Check the output voltage function.
By the way...  make sure the battery is charged before you begin testing, too.
old field guy
Thx OFG.
These meters are less than two years old and come with a 2-year OEM calibration validity.
And yes, their batteries were fully charged too.
I still have my old original motor operated Evershed Vignoles "megger" . Plan to use that as a calibrator and see how these "state-of-the-art" digi meggers fare.
I must admit that my trust in all digital metering is taking a beating today.
Muthu
www.edison.co.in
Edison, are you discharging the insulation between these tests? That could be causing the differences in your readings. It is very common to see a differnce of 10x from your 30 second reading and several minutes later as your cap charging current and absorbsion currents decay from charging and polarizing the insulation in an inductove system.
Zog
Yes, I discharged between the tests (though it was only 500 V and the winding is pretty much like LV motors - no solid insulation like MV motors for much of polarization to take place). And I repeated the test and the values are in the range I've posted. Well, at least they're consistent in their errors, I guess. :)
Muthu
www.edison.co.in
Back to the hand crank.....