(OP)
What is the maximum water pressure in private service mains? The question was asked by a sprinkler fitter who was tested on it.  Thank you in advance.  

RE: Private Service Main

Probably depends on the pipe material and joint type.

Ductile iron flanged piping goes from 150 psi to 350 psi depending on pipe diameter.

This is according to my US Pipe and Foundry catalog.

HDPE pipe goes up to ~200 psi.

RE: Private Service Main

NFPA 24 has no pressure limit, and this standard governs private service mains. The pipe must be designed to supply the demand at a minimum pressure of 150 PSIG. The minimum hydrostatic test pressure is 200 PSIG or 25 PSIG over the design pressure if the operating pressure is > 200 PSIG.

RE: Private Service Main

Accessories such as hydrants, valves, test headers, etc. are rated to 175-250-300psi.So keep that in mind.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources