Parallel Transformers at different tappings?

Parallel Transformers at different tappings?

Parallel Transformers at different tappings?

(OP)
Hi looking to tap down two identical 11kV/415V transformers these will be done isolated one at a time, however they will need to be momentarily parallelled while they are at different taps I know the risk of circulating currents and fault rating risk of parallel fed LV switchboards. How can I pre-determine what the circulating currents may be to prevent risk of trip?
Has anyone experience of doing this before?  

RE: Parallel Transformers at different tappings?

You can model the transformers as parallel impedances, with a voltage source in one parallel path equal to the no-load voltage difference between the two unequal ratio transformers.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources