gfci tripped by variable speed drive
I have a variable speed drive that operates on 120 VAC single phase in order to drive a three phase motor as an output.
However this drive trips GFCI outlets where ever it is plugged in.
PWM changes don't help.
I am contemplating a common mode filter but this seems hard to find in high power ratings.  Need 15 Amp capability.
Also considering an isolation transformer.
Any other ideas or comments ??
RE: gfci tripped by variable speed drive
It trips other (distant) GFI outlets?
Either an isolation transformer or a VFD with native sinewave (sinus) output. GFIs with 30 mA is difficult. I can imagine that you are using an even lower trip limit. Then I would say you cannot use a GFI with any PWM inverter if you do not use an isolation transformer. Capacitive current leakage from stator windings to stator iron will trip it. Some drives also have filters built-in. That makes it even worse.
Gunnar Englund
www.gke.org
ve
No it only trips the one it's plugged into.
Skoggs,  I think you might be right.
Only rarely, with really small VFDs, can you plug them into a GFI and NOT have them trip. If you look at the manual it will likely state the leakage current.  You will see it's probably over 5mA which is the typical GFI trip level.
I have the smallest TECO 1ph input unit here in my living room on piece of furniture.  Let me try it in the GFI it will eventually be plugged into.... I need a grounded extension cord...  I have a grounded extension cord sitting on the coffee table...
Hey! I'm in luck! It doesn't trip the GFI outlet.  I really expected it to.
So, as I mentioned, some will work, especially if they're small enough.
Keith Cress
Hey, Smoked!
Was the motor frame grounded when you tried that?
The most current flows through motor capacitance to ground. But only if motor is grounded. Was it?
Gunnar Englund
www.gke.org
Yes sir! Well grounded to the earth in the same cord.
Keith Cress
Can high frequency noise in the power lines also trip the GFI?
Good o'l reliable safetyminded Smoked..
Gunnar Englund
www.gke.org
Zapped
Awesome page on GFCI history
thanks