Installation of Magnetic Flow Meter
3

Installation of Magnetic Flow Meter

Installation of Magnetic Flow Meter

(OP)
I have a situation where a client wants to installa a flow meter horizontally at about a 20 degree angle. My suspicion is that it will not work because I was of the impression that the meter needed a laminar flow.

The meter is measuring raw water flow in a waste water treatement plant.

Please advise.

Please advise.

 

RE: Installation of Magnetic Flow Meter

Mag flow meters can usually be mounted anywhere from horizontal to vertical.  You do always need to install them in a straight section of pipe, at least about 5 pipe diameters downstream from any elbows or valves.
If the pipe does not typically run full, you can pipe it in, with a U or V shaped arrangement to create a low spot where the pipe does run full.
The best idea would be to talk to the people that make the flow meters, and discuss your application.

RE: Installation of Magnetic Flow Meter

EVERY magmeter manufacturer has a page in its manual similar to the one below with recommended installation practices.  

Note that angled installation is an example, with the requirement that the pipe be full.

Experience shows that if installed on an angle with flow downwards, EVERY problem with the magmeter will be blamed on "partially full pipe".




 

RE: Installation of Magnetic Flow Meter

A slope is OK provided the flow is up, not down.
Orient it so the electrodes are across the pipe, not vertical.
I have installed a mag with flow in the downward direction (vertical pipe)where it was the only choice however the signal from it is eratic. I think what happens is gas bubbles entrained in the fluid travel up while the fluid travels down and every now and then a bubble sits at the electrode disrupting the signal.
Roy

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources