Why it is better to use 4-20mA Than 0-10V signal. And friends on what basis 4 and 20 nos have been decided.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 4-20 mA Vs 0-10 V ?
1. A current loop signal is less susceptible to interference and noise, particularly over longer distances. The transmitter produces a load independant output (within the range of the transmitter) so volt drop is also generally not a problem.
2. The 4mA zero offset allows you to detect failure of the transmitter. With 0-10V, does 0V mean zero measured parameter, or transmitter failed ??
As to why 4-20mA ... who know ??
RE: 4-20 mA Vs 0-10 V ?
4mA was adopted to indicate a quantity zero signal so that if the signal is 0mA it would indicate a fault of some kind.