reactor air requirements?

reactor air requirements?

reactor air requirements?

(OP)
I'm getting conflicting air requirements from two different modeling programs. The aeration basin has three zones with design DO levels of: 0,1,and 2 mg/l, respectively. There is a recycle flow from the third to the first zone for denitrification.
One program says the second and third zone need nearly the same volume of oxygen. The other is saying the second zone requires approximately 70% of the oxygen demand.

The second seems to go along with EPA "purple book" guidelines, but I dont believe those were based on a de-nitrification plant.

Any thoughts?

Thanks,

Mike

RE: reactor air requirements?

Do your programs address the energy required for mixing? If the air flow is less than the minimum flow required for mixing, then a mechanical mixers should be used.

RE: reactor air requirements?

(OP)
I dont believe the programs do, but we have thought of that. By my calcs during the lower flow and loading conditions we need a lot more air for mixing then the bugs in the basin do. Currently they have no mixers in the aerobic cells. The DO control system we're installing will have operator set minimium air flow set points reguardless of DO. If in actuallity we find we're spending time running at min. air flow with high DO levels we'll quickly be installing some mixers.  

RE: reactor air requirements?

If you do not put at least 20 SCFM/1000 cu. ft of air into the basin, the solids will settle on the basin floor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources