ASCE 07-05 section 7.9 discusses sliding snow requirements for any roof above another roof.

I'm curious if this load should apply for dormers, where the roof above is not very high above the roof below?

Secondly, does sliding snow or drift loads apply to roofs at a pitch change?

Any comments?  I've attached a picture for your review.

RE: Sliding Snow Loads

Question 1--the answer is yes, but there won't be much sliding snow, because the dormer roof is so small.

Question 2--the answer is no.

DaveAtkins

RE: Sliding Snow Loads

(OP)
Thanks, Dave.  I would have thought that the sliding snow would be small for that dormer.  However, it ends up going from ps=25.2psf to sliding of 100psf over 15 feet.  That ends up being pretty significant.

RE: Sliding Snow Loads

Your numbers don't make sense.  How wide is that dormer--10 feet?  Then each side of the dormer receives 5 feet of snow from the upper roof, spread over 15 feet--something like 8 psf, not 100 psf.

DaveAtkins

RE: Sliding Snow Loads

(OP)
one correction.  the flat snow load = 25.2psf.  the sloped snow load = 20psf.  as I see it, the sliding snow load + superimposed sloped load = 20psf + 0.4 x (pf =25.2psf) * (W=8ft) (ridge to eave) = 100psf.  

I suppose one area of discussion could be in ASCE 07-05, section 7.9, is the defintion for W as "eave to ridge."  I'd say that this defintions would more clearly read "overhange to ridge."  If it truly is eave to ridge, this would reduce my total load a bit.

Am I missing something?

RE: Sliding Snow Loads

(OP)
Upon re-reading the section, I think I missed a very important part.  The code reads, "...The total sliding load per unit length of eave shall be 0.4p fW, where W is the horizontal distance from the eave to ridge for the sloped upper roof."

I missed the part about per unit length "OF EAVE."  I thought the 0.4*pf*W was per unit lenght over the 15 feet, so I interpreted the total load as a uniform load over 15 feet, not the total load / 15ft.

I think what you were getting at was this:
0.4 * 25.2 * 8 = 80psf / 15ft = 5.3psf
Ps = 20psf + sliding snow = 5.3psf = 25.3psf over 15 feet.

Is this what you were trying to say?

RE: Sliding Snow Loads

Yes.  I was just throwing around rough numbers, but I knew the load is to be spread out across the 15 feet.

DaveAtkins

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources