Butt weld on cap plate.
Good morning,
I would like to know the correct way to calculate the maximum load a complete penetration butt weld can take.
The weld is on a 25 thick cap plate welded to the end of a piece of 150x150x9 square hollow section.
On top of the cap plate is a lifting lug.
The plate, lug, and steel section are all grade 350.
I have read that I can take the effective throat as the thickness of the thinner plate - in this case 9mm.
I have also read that for a full penetration butt weld, calculation is not necessary because
the filler metal strength is at least as high as the parent metal strength of the weaker part joined
and the throat thickness of the weld is equal to the thickness of the plate,therefore
the butt weld may effectively be regarded simply as replacing the parent material.
I have done a calculation but would like to check to ensure I am correct.
Any help would be greatly appreciated.
Regards.
Regards.
RE: Butt weld on cap plate.
Let's assume outside.
First, you need to be sure you have a complete penetration weld. Has nondestructive testing been done?
Assuming you have a complete penetration weld, the tension of the system is then calculated on the thickness of the hollow section, using the material properties of the hollow section, not the weld.
The weld is on the outside, so in tension.
Non destructive testing will be done, and the part will not be used unless it passes.
Could you please show me an example of what you mean by calculating on the thickness of the hollow section?
I have attached a brief drawing of the arrangement in question.
I am, however, interested if Ron has any comment because I'm not familiar with any differences in a full pen butt weld with respect to welded side.
1. The weld metal must be as least as strong as the steel so you need to use E48 electrodes (fuw=480 MPa) for grade 350 steel (check this).
2. The load won't be evenly distributed along the welds so you need to consider only the effective lengths of weld.
See sketch attached.
Thanks so much for your comments so far.
The electrodes to be used are 480 Mpa.
So far I am not interested in the lug - just purely the cap plate. I can understand the load not being evenly distributed along the weld, but if I were to pull directly on the lug\cap plate it would be evenly distributed - correct?
The effective length of the cap plate weld is 600mm - 150 x 4. Correct?
Regards.
Michael.
Timing has a lot to do with the outcome of a rain dance.
Why don't you make the lug extend into the tube and weld it to the inner face with 4 fillet welds, then add 2 thin cap plates to keep the rain out? This would work for relatively low lug loads, where you don't need too much weld length. Alternatively, you could cut 2 grooves (as long as you need) into your tube, insert the lug into the grooves and make the fillet welds from outside?
tg
If you stay with the direct tension design, the lower strength material will control, that being the interface between the weld and parent material. Use the thickness of the tube to compute the effective stress area and use the strength of the tube....the weld strength doesn't matter since it should be greater than the parent material.
It is not uncommon to see a 50% reduction in tensile strength in the through thickness direction of the hot rolled plate.
Best regards - Al
The design is the way it has been done for some time, so not my place to change it. (I am relatively new here). I know it works as the welds are NDT tested and then load tested.
Just for my own information I was curious to see a calculation done on them.
I did a calculation, but to me perhaps a little simplistic and perhaps incorrect;
f = 480Mpa/3 = 160 Mpa allowable stress
F= flt = 160x600x9 = 86400N l=600mm t=9mm
86400/9.81 = 88073.4 N
= 88 Tonne.
Michael.