I have a question with regards to wind loading on a wall stud.
When designing a wall stud for out of plane wind loading, I always assume a Component & Cladding wind load along with gravity loads (Dead & Roof Live) for the roof with the revelant load combinations (i.e. D+W, D+0.75(Lr+W)).
For some reason, people in my office have been neglecting considering a positive wind load on the roof in addition to the wind load on the wall, which would increase the axial load in the stud.
My question is, if I were to start considering wind load on the wall and on the roof in the design of the stud, would I use Components & Cladding loads for both pressures. It seems too conservative to take C+C loads to design an element that is receiving that load from two surfaces. C+C loads represent the maximum intensity that can be expected over a small area. It seems very unlikely that could happen on both a wall and a roof at the same time. This idea is based what I learned from a professor at my school that is on the ASCE7 wind loading committee. He seems to like the idea of the summarily dismissing anything that collects load from two surfaces as MWFRS.
When designing a wall stud for out of plane wind loading, I always assume a Component & Cladding wind load along with gravity loads (Dead & Roof Live) for the roof with the revelant load combinations (i.e. D+W, D+0.75(Lr+W)).
For some reason, people in my office have been neglecting considering a positive wind load on the roof in addition to the wind load on the wall, which would increase the axial load in the stud.
My question is, if I were to start considering wind load on the wall and on the roof in the design of the stud, would I use Components & Cladding loads for both pressures. It seems too conservative to take C+C loads to design an element that is receiving that load from two surfaces. C+C loads represent the maximum intensity that can be expected over a small area. It seems very unlikely that could happen on both a wall and a roof at the same time. This idea is based what I learned from a professor at my school that is on the ASCE7 wind loading committee. He seems to like the idea of the summarily dismissing anything that collects load from two surfaces as MWFRS.






RE: Wood Wall Stud Design
I disagree with your professor, the pressure on the corner of the wall and the suction on the corner of the roof are both caused by the increased air velocity at that corner, however I'm not sure it goes to the stud and purlin.
How do you get a positive pressure on the roof?
Michael.
Timing has a lot to do with the outcome of a rain dance.
RE: Wood Wall Stud Design
If your roof pitch is less than 45 degrees it won't see positive pressure per any of the tables in ASCE 7, but ASCE 7 also requires a minimum 10psf wind load. This to means you have to consider positive wind on the roof no matter what.
RE: Wood Wall Stud Design
RE: Wood Wall Stud Design
So you would have both bending and axial in the stud at the same time, due to wind.
RE: Wood Wall Stud Design
RE: Wood Wall Stud Design
Depending on your stud size you can get a very large increase in Fb for (Cr factor) wind. You have to meet special criteria, but it is pretty standard and it will probably always be met except for some unusual circumstances.
For example, 2x4 Cr can be increased from 1.15 to 1.5.
RE: Wood Wall Stud Design
In ASCE 7-05 Chapter 6 Commentary they give examples of components ...fasteners, purlins, girts, studs... So, C&C wind loads would be correct loading for stud design.
RE: Wood Wall Stud Design
Can you point me to where Cr = 1.5 in the NDS? I'm not seeing it. Both sections 4.3.9 and Table 4A show only the 1.15.
Were you perhaps looking at CF?
RE: Wood Wall Stud Design
Maybe ash060 was referring to IBC 2306.2.1 where in lieu of Cr =1.15 you can use the increases given in the chart, provided you meet the associated criteria.
RE: Wood Wall Stud Design
It is Table 3.1.1.1 under section 3.1.1 "Wall Framing".
I think that there is a later version of the special provisions, but I do not have it
RE: Wood Wall Stud Design
page 11 0f 33 showes Table 3.1.1.1 Wall Stud Bending Stress Increase Factors:
2x4 1.5
RE: Wood Wall Stud Design
RE: Wood Wall Stud Design
But I CANNOT believe a positive wind load (pushing down on the roof) will ever be greater than snow load or minimum roof live load.
Am I missing something?
DaveAtkins
RE: Wood Wall Stud Design
D+W
D+0.75Lr+0.75W