Location of Lightning Arrestors in Service Entrances
Hello
Query regarding location of Lightning Arrestors
I am working on an arrangement wherein the utility provides 230kV supply at their substation. At present we are the only entity tapping of from the utility substation but others consumers may be included in the future. The distance between our substation and the utility substation is about 300 feet(100m).Utility is providing a lighning arrestor at the service entrance of their substation.
My query: Is an arrestor required at the entrance of my substation considering the short length of line between the 2 stations.
Also,transformers in my substaion have lightning arrestors mounted on them. Details of the utility substation arrestor are not available. Project location: North America. Thanks in advance for your inputs
RE: Location of Lightning Arrestors in Service Entrances
Second, you have to install at entrance of line to protect CT,DCP,CB,DS equipments.
Even though the 300 feet(100m) of distance could be covered by transformer lightning arrestors,
you should be carefull if there is condition of Line Disconnecting Switches opened
and some equipment(CT,DCP,CB,DS) are at entrance line side of travelling waves.
Thanks for your inputs
viswa
I did not understand.
If you have an entrance of line in sequence: TP,DCP, DS before to connect at busbar, you should include
lightning arrester at line incoming anyway!