Parameter estimation of transmission line

Parameter estimation of transmission line

Parameter estimation of transmission line

(OP)
Does someone have working experiences to calculate transmission line parameters (R, X, and/or B) based on real-time telemetries at line terminals(P, Q, KV)? This is to verify line parameters calculated by system planning. It is important for relay settings.

RE: Parameter estimation of transmission line

You need I and V, magnitude and phase angle, at precisely the same time.  Synchrophasors are what you need.

RE: Parameter estimation of transmission line

(OP)
Thx. My question is if someone really did the test and/or calculation. "Synchrophasor" can be obtained by PMU (phasor measurement unit) or EMS (energy management system in control centers) estimations.
 

RE: Parameter estimation of transmission line

It's trivial if you have the synchrophasor data.  I'm not aware of an EMS the has PMU capabilities.  The calculation has to be done using data from both ends gathered at precisely the same time, but then it is just a simple power system analysis homework problem where you are given the voltages at both ends, the current through the impedance and need to calculate the impedance.  Piece of cake.  The only difficulty is in obtaining the data.

RE: Parameter estimation of transmission line

Calculation of positive-sequence impedance by classical means is pretty accurate, so calculating with synchrophasors is not very important.  It's the zero-sequence impedance that involves a lot of estimation for classical calculation.  With balanced loads, you can't do it with synchrophasors either.  You need to have a ground fault or a lot of imbalance.
 

RE: Parameter estimation of transmission line

Yeah, good point.  Zero-sequence is very difficult to get nailed down.  But for the purposes of a system model used for state estimation, all that is needed is the positive-sequence network.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources