Std ATEX ExD IIG = NEMA 7 ?

Std ATEX ExD IIG = NEMA 7 ?

Std ATEX ExD IIG = NEMA 7 ?

(OP)
Hi everybody!!!!

I have a question, if I want to use a NEMA 7 enclosure, you know that NEMA 7 are made of aluminum exent of copper and enclosures with standard ATEX Eexd IIG have enclosures explosion proof of aluminum exent of copper...can I use an enclosure of std atex AS A NEMA 7??? DOES STD ATEX EEXD IIG HAVE CLASIFICATION 1 DIV 2 GROUP ABC AND D???

Regards.

Roland

RE: Std ATEX ExD IIG = NEMA 7 ?

If it doesn't say NEMA 7 then I seriously doubt it. Certainly NEMA 7 doesn't mean jack in the ATEX world.

That ATEX certification looks incomplete anyway, there should be a gas group and temperature class listed too. The information presented says it's a flameproof enclosure for surface (i.e. non-mining) duty with gaseous flammables but exactly which gases and which maximum surface temperature isn't stated.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Std ATEX ExD IIG = NEMA 7 ?

What's in the enclosure?

RE: Std ATEX ExD IIG = NEMA 7 ?

Permit me to offer the corollary to ScottyUK's post: "EEx" doesn't mean jack in the NEC/US domestic world.

The certification also falls short in US marking requirements and pretty much for the same reasons (unspecified gas and temperature classifications) In addition, the NEC requires an "AEx" rather than "EEx" mark to indicate it was certified to a US "Zone" standard.

Oddly enough, with a proper temperature classification mark, it may still be fine in Class I, Division 2.  

RE: Std ATEX ExD IIG = NEMA 7 ?

First time I have heard of the 'AEx' marking - I will keep an eye open for it. Is that a relatively new requirement or have I just missed it in the past?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Std ATEX ExD IIG = NEMA 7 ?

It has been part of the US National Electrical Code requirements since the 1999 Edition. [Section 505.10(b)(2)(c) in 1999, Section 505.9(C)(2)(3) in 2008] It's similar to CENELEC appending the leading "E" to IEC's basic "Ex."

RE: Std ATEX ExD IIG = NEMA 7 ?

Thanks - something new I have learned today, and it's still only 0712 this morning!

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources