Transformer Imbalance Guidance

Transformer Imbalance Guidance

Transformer Imbalance Guidance

(OP)
Does anyone have any guidance regarding how "imbalanced" the phases can be with a three-phase, 480 to 240 10kVA tranformer? We'll have a balanced 3-phase source, but our output (load) will have single-phase components and power supplies turning on and off. We won't be able to keep them balanced. Are there any design rules or guidelines that I need to follow regarding imbalance loads?
 

RE: Transformer Imbalance Guidance

Imbalance does not hurt the transformer as long as the most heavily loaded phase is not overloaded.  The problem might be voltage unbalance.  This should be limited to 5% or less.  You will need to calculate this based on the transformer impedance and the load.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources