2006 IBC Table 2306.4.5
This table gives allowable shear values for gypsum board.  Are these values for applying the board to one side only?
I cannot find where it states whether it is for one side or for both sides anywhere. It is implied in 2305.3.8.
RE: 2006 IBC Table 2306.4.5
Though I am at home and don't have the code in front of me, I recall designing with gypsum shear walls before ( with an icc report, i beleive) and I remember that it did not allow an increase in loading for sheathing on both faces of the wall. Hopefully that's a start for you.
IBC 2006 section 2305.3.9 discusses summing "shear capacities" and refers to material of the same type on both faces of the wall and also refers to gyp board.
This section refers to "summing" and values being "cumulative". This section wouldn't make any sense if the already tabuluated shear values listed were intended for sheathing on both sides.
I take the gyp shear values meaning applied to a single face.
haynewp is correct.
I will emphasize his statement that both sides have to be the same thickness and nailing.  Otherwise, double of the lesser value would have to be used, which would be stupid.
Mike McCann
MMC Engineering
Correct, one side.
You can sum each side, limited by the lesser of the two sides.
Only note I wanted to add was in residential you are allowed to sum unlike materials together.  OSB can be added to gypsum board.  I don't really agree with this since the two materials perform differently, but you can do it.
Jim Houlette PE
Web: www.evstudio.us
Online Magazine: www.evstudio.info