60hz transformer on 50 hz
We have one transformer 1000kVA,4.160kV/0.480kV,Delta/Star, 60Hz.If we coonect with 3.3 kV, 50 hz , will that work ? . I need to get 380 volts at secondary.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: 60hz transformer on 50 hz
(I'm assuming you meant 480 V, not 480 kV)
But you won't have a 1000 kVA transformer any longer.
Neil
That's what they always say....
You should add a new nameplate indicating the reduced kVA rating.
The new KVA rating will be 1000 KVA x (3300/4160) = 793 KVA. Call it 790 KVA.
To calculate the new impedance you will have to know the X/R ratio of the transformer. It may be easier to just connect a Variac to the primary, short the secondary and measure the impedance voltage, if you need this information.
Bill
"Why not the best?"
Jimmy Carter
Imagine a case you have a 60 Hz trf with flux density 20 % less than normal.(today's trfs have 1.7 T as B)Then you can connect to 50Hz.You can work on the same kVA rating.But percenatge impedance will come down by 20 % so that voltage dip with loading will be less.
Muthu
www.edison.co.in
But to reduce the flux density you have to reduce the voltage as described above.
Keith Cress
In real practical applications, it is always a FAQ with same voltages.Once again sorry for wrong answer.
AFAIK, very important only one thing:
U/f=const ( as Dave pointed)
Best Regards.
Slava
Bill
"Why not the best?"
Jimmy Carter