Install VFD on positive displacement blower??
My client is using 4 positive displacement blowers with timer control in his wastewater treatment plant to provide oxygen to the process. Recently, he proposed to install VFD on these blowers to control the amount of air flow and reduce energy consumption. Since the blowers are supplying constant discharge pressure to the process, it seems to me that it is impossible to adjust the speed of the blower by using the VFD. I was thinking about installing a inlet vane in additional to VFD so that the blower can be reduce in speed as well as maintaning the specific discharge pressre. Would any one has comments to this setup? Thanks in advance!
RE: Install VFD on positive displacement blower??
Are all the blowers going to be running in parallel or do they run their own aerators?
Keith Cress
The plant has total of 4 blowers, 2 aerators. Each blower has an independent run/cycle timer. They typically run one blower in each aeration tank continuously, and then maybe cycle a second blower on/off during the day.
A VFD can be very effective on a PD machine. The reduction in power consumption is much less than it would be with a dynamic machine (like a fan or centrifugal compressor), but it can still be substantial.
David
A VFD itself by slowing down the speed of the blower motor would not satisfy the discharge pressure requirement. Am I correct?
Answer is "maybe, but maybe not", the depth of the aerator outlet and/or its opening hole sizes may do more to limit the discharge pressure than anything the blower does, to some limiting lower speed limit for the blower. Get a good set of operating curves and/or software from the blower manufacturer and run various cases to see how far down (in RPM) you can run it and still make bubbles come out of the pipes.
The VFD manufacturer can probably give you a good idea on the motor side.
On the pump side you, the blower vendor can't tell you this without knowledge of your system.
Without knowing the information above, success will be a crap shoot.
Let's say that the reason you need a particular pressure is to overcome hydrostatic pressure as you blow air into the bottom of a pond for aeration. The blower will overcome the pipe friction and the hydrostatic head at any speed, but the friction component will change dramatically as you change your flow rate. It is still the same thing, the compressor will keep increasing its discharge pressure until either: (1) it overcomes resistance to flow; (2) it runs out of hp; or (3) it lifts a PSV (or breaks something). One of those three things has to happen at every speed.
David
"When VFD reduces the speed of the blower, isn't the DP will also reduced? Since the process requires constant discharge pressure, I was thinking VFD alone cannot meet the goal.", shows you have a reasonable handle on the logic and effects of installing a speed control and that itis totally correct. We engineers should know that you don't get a free lunch; everything has a disadvantage that comes along with its supposed advantage, so don't let anybody change your mind without solid calculations to back it up.
A speed control (taken by itself) has a tendency to reduce BOTH discharge pressure and flow. If you need both of those functions, there could be a big advantage to using a VFD. If you don't, there may be only disadvantageS. If your system curve shows that it also reduces its pressure requirements when flow reduces, it could be a good candidate for speed control. If you system curve shows that you need constant pressure when flow reduces, be very weary of speed controls.
If you install a vane (valve) with a speed control, in effect you will have to run at a higher rpm to increase the pressure by at least an amount equal to what the vane will lose. Essentially that is the same manner that a fixed speed blower without speed control works, the only difference may be that you might be able to run at a somewhat lesser speed than blower's rated fixed speed. Maybe not. You might wind up having to turn up the speed to almost the same or even higher than fixed speed, if you're near your max flowrates. Two big disadvantages! If you need to run at nearly fixed speed with the vane installed, you may save nothing. That's the question you need to answer, however with fixed pressure requirements for all flows, the likelyhood you will save power and money with speed controls is very doubtfull.
Check it carefully.
"Pumping accounts for 20% of the world's energy used by electric motors and 25-50% of the total electrical energy usage in certain industrial facilities."-DOE statistic (Note: Make that 99% for pipeline companies) http://virtualpipeline.spaces.live.com/
the discherge pressure isn't defined by the rpm, but rather defined by the system back pressure (provided flow>internal leakage).
David
flow is oriented away from pump discharge,system pressure is oriented towards pump discharge pressure,hence system back pressure,pump discharge pressure.
During the time of one PD cycle, if certain conditions are met, a specific mass of gas is ejected into the system segment. Yes, pressure in the PD must be slightly higher than system inlet pressure in order for the discharge valve to open. The critical question becomes, how much higher.
Well, the pressure must be higher by 1.) enough to open the valve; we'll say a pretty small amount there, and 2.) The cylinder pressure must be high enough such that, if the gas is ejected into the system segment, the resulting pressure of the segment equals the initial downstream pressure plus the increase in pressure due to the entering mass of gas from the compressor, minus the decrease in pressure due to the mass of gas exiting the segment to downstream points. So, yes, the mass of gas coming from the PD's cylinder affects the system pressure. And we also note that the downstream pressure affects the compressor's discharge pressure. Just as you say. However, we must also look at the mass of gas entering the system segment from the compressor, as we have shown that it affects the system pressure too. So, is not the mass of gas entering the system a function of the PD's cycle volume, and the mass of gas entering the system will increase with decreased cycle time? And, therefore isn't the mass of gas entering the system hence also a function of RPM? There is no way for the compressor to create an internal pressure greater than what is needed for the valve to open and eject its gas into the system downstream. It can't create any pressure higher than that, because the compressor's outlet valve is open by then. If it tries to increase pressure more than that, mass simply escapes the cylinder into the downstream segment. It is possible that the downstream segment pressure tends to increase, if and only if the downstream segment's net mass at the end of the timestep is greater than the original mass at t0, or decrease if net mass is less. If incoming mass equals outgoing mass, the system remains at the same operating point, so flowrates and pressures remain as they began at t0.
Don't try to separate the compressor from the system, or the system from the compressor. They function together as a unit. Each depends on the other equally, except for the small differential pressure needed to open the valve and pack the first segment of pipe. The length of pipe making up that segment that we need to consider is the same distance that the pressure wave will travel, at the velocity of sound inside the pipeline, during the time of one compressor cycle.
h
Draw a straight line across any of the charts, to show the operating line for a blower discharging to a constant system backpressure. Reducing RPM drops the power required, as volumetric flow is decreased. The power decrease isn't linearly proportional to flow, due to slip, and certainly is not as dramatic as the square-law decrease in power if pressure is allowed to decrease, but it's not insignificant.
Here's another view, using a set of data tables:
http://www.omega-inds.com/roots-blowers.htm
Take the Whispair 44 blower, one that I'm quite familiar with, operating at 5 psig. At 1500 rpm, it puts out 82 cfm, consuming 3.5 bhp. Drop the speed to 900 rpm, and it puts out 28 cfm at 2.1 bhp. I.e. the power dropped proportionally to the rpm decrease, but the cfm decreased a lot more.
Understanding how much power savings could be achieved would require more info. than currently given. But it wouldn't be zero, unless the system is designed in the top right corner of the blower's operating envelope.
Sha-zam!
http://
since the machine itself is a reliable piece of equipment
(provided with a sync gear)
on a constant speed machine, there is a requirement for an unloading valve, to coope with flow fluctuations.
if VFD can keep motor torque within shaft working envelope,
the unloader valve as a failing mechanism could well be proven obsolete.
(to keep motor running with 0 flow)
Mike Halloran
Pembroke Pines, FL, USA
If you take a positive displacement pump with minimal slip and dead head it, it will increase pressure until the motor stalls or something breaks.
You need to determine how motor maximum torque is reduced as speed is reduced to get a pump curve. Then you need to determine how system pressure behaves with decreasing blower speed.
This second item changes depending on what you do. If you have a backpressure valve controlling pressure, maybe system pressure stays constant meaning that torque increases as the blower motor slows down. If there's a fixed orifice or normal system resistance then pressure drops as the square of the speed, and the torque reduces. I'm fairly confident that at decreased VFD speed, maximum motor torque will decrease. So, a backpressure valve may not work well with a VFD. A fixed orifice probably work quite nicely.
Until you work this out, I doubt you can definitively answer the qustion "will it work" without an after-the-fact test.
Both centrifugal and PDs have pump "curves", see attached, that can vary significantly with RPM. Of course the curve in a PD pump is more of a straight line with negative slope.
While it is true that a pd pump running at constant speed has relatively little variation in flow (when talking about a "normal" system curve), varying RPM affects flow in a centrifugal pump, a pd pump and the system.
The operating point depends on BOTH pump and system characteristics for either type of pump.
The only problem with a PD pump is there is no problem.
Draw the curves for variable speeds and you will see that you can get from 0 to runout flows in either type of pump.
Because of the relatively limited flow range with a fixed speed PD pump, a flow control valve on a fixed speed PD is virutally useless, which is why most drives for PDs are variable. A variable speed device combined with a control valve is belt and suspenders in most cases. Simply not needed. RPM can be varied to accomplish the same thing. jThey might be of use, if system head changes radically and fast, where a valve might be adjusted more quickly than the motor rpm, but I would think that circumstance is probably rare. A pressure control valve (used as a relief valve), does make sense.
It would also make little general sense to use a valve with a centrifugal pump with a VFD. Belt and suspenders again.
Flow control valves with a fixed speed centrifugal pump does make sense, due to the high flow variations possible, but used a a pressure control valve, probably is not necessary, as long as the system will tolerate the pump's shutoff pressure.
The secret to knowing what type of pump to use and what valve, if any, or if you need VFD or not, is to look at BOTH the system curve(s) and the pump curve(s), whether its a centrifugal or PD pump, the answer is there, right at the operating point(s) <where both curves intersect>.
If you look at the attachment of curves for a generic PD and centrifugal pump, combined with the flowrates you know that you must be able to run, everything becomes quite apparent.
If your customer has one aeration basin, then controlling only the VFD should work, but if he has more then one and wants to independantly control the level in each tank, I think using the control valve with the VFD controlled blower would work better.