1920's lime and gravel foundation
I recently inspected an old foundation that has a cement stucco on the interior. There are a couple locations where the stucco has broken off, and the foundation wall has been exposed. At these locations (and I'm assuming along the entire wall) the wall has deteriorated and just brushes off. The wall is composed of a gravel and what I'm thinking is a lime mix and I'm wondering about the best way of repairing the foundation walls. If I try and put concrete against the existing wall am I going to run into future problems with having a portland cement product in direct contact with a lime and gravel product? I know it's an issue for brick walls, but I'm not sure if that's the same with this foundation wall. I was thinking of shoring, removing the stucco and brushing off the loose portion of wall and placing a new finish - 6" or more on the inside of the wall.
RE: 1920's lime and gravel foundation
Okay, so you need your new mortar to creep. I would suggest looking into a mix design that uses lime as well as cement, and also you're going to need to be very careful about how you do your pointing. I hope you have access to an experienced contractor who has handled lime mortar masonry restoration before.
One other detail: Are you dealing with stone or is this brick? Since you're at the foundation, I would presume stone, however well-fired dark red brick laid directly on the ground in a step-out pattern is not unheard of for an old foundation. If you have brick, I would suggest not removing broken units; At the foundation it is simply too dangerous an undertaking.
Hopefully some of our other friends out there will chime in with useful contributions. Good luck!
Cheers,
YS
B.Eng (Carleton), P.Eng (Ontario), MIPENZ (Structural-New Zealand)
Working in Canada, and missing my adoptive New Zealand family... at least I brought the little Kiwi with me!
Worst case scenario is they replace it, but I was hoping to avoid it if anything safe could be done.
Thanks for your thoughts - I'm trying to brainstorm with as many people as I can.
If the concern is the axial capacity of the existing walls, a new wall on the inside won't help much as it will not be under the load and will not be resting on a footing.
BA
It is also possible that you may have soluble sulphates in the soil and that the early cement wasn't sulphate resistant.
It may be that the only option is to underpin and remove the existing foundation wall.
Dik
I agree with our estimed colleagues; You are most likely going to have to replace this foundation. I've provided new foundations adjacent to existing (insufficient, failing, etc) foundations, needled the wall above and carried the existing wall in this manner. It is difficult, expensive, and requires access to both sides. Otherwise you can repair/remediate the wall by needling the existing onto temporary founds (again, normally requiring two sides of access) and remove/replace/repair the existing foundation in-situ.
Now just in case I'll point out that Needling is the process of removing some bricks (often in multi-whythe walls) and passing a beam perpendicularly through the hole to carry the bricks above while you work on/replace/remove the bricks below.
Okay, so there is still yet another possible solution: Replace the existing load carrying system with a new wall and foundation; This is not cheap, but is sometimes quite practical... I've seen this done (in a magazine), though never attempted it myself. Essentially you are being wholly unsympathetic to the existing (and possibly historic) structure, but it is on occasion the right way to go as it can permit full change of use/expansion/replacement of the structure.
Good luck and let us know how it goes,
Cheers,
YS