UL 508A Disconnect

UL 508A Disconnect

UL 508A Disconnect

(OP)
I need a listed fused disconnect for a 120vac, 20amp, single phase panel.  It needs to satisfy both UL and NFPA79 with the interlocking requirements.  These are small table top cord connected pieces of equipment with limited panel space available. I don't have the room or the $$$ for a 3 phase fused disconnect and leave the other two phases open.  I've look around and see alot of load switches with post fusing but this does not satisfy UL.   

RE: UL 508A Disconnect

NFPA 79 - 5.3.1.4, 5.3.2 and 5.3.3.2 allow for an attachment plug and receptacle for the supply circuit disconnecting device.

I wonder if that combinded with UL 98 listed Bussmann P/N CCP-1-30CC would suffice?

see:
http://www.cooperbussmann.com/pdf/1559cce7-6434-4098-b8e3-a64dc373fd0f.pdf

David Baird

Sr Controls Designer
EET degree.
Journeyman Electrician.

RE: UL 508A Disconnect

(OP)
Thanks for responding!!
One problem is UL 508A won't allow the attachment plug to be the disconnecting means.  I'm stuck between NFPA79 and UL requirments.  Any advice would be appreciated.

RE: UL 508A Disconnect

See UL 508A 28.5 Cord Connected quipment.

RE: UL 508A Disconnect

(OP)
I agree you with you Reddog you can connect with cord but my understanding is you can't classify the attachment plug as the disconnect means if UL'd like you can with NFPA 79.  There isn't any listing in section 30.1 of the 508A for attachment plug. Am I overlooking something here?

RE: UL 508A Disconnect

(OP)
I like it, I just wish I could find a single pole like this for 120vac application to keep the price down.  Thanks for helping out!!

RE: UL 508A Disconnect

What is the HP rating of this controller?

RE: UL 508A Disconnect

(OP)
This is a 1/250th HP torque motor.

RE: UL 508A Disconnect

Joe,
I think I might have a workable solution for your consideration:

Interlock your enclosure door with Pilz magnetic safety lock so that the door is held locked unless you unplug the supply cable. This satisfies NFPA 79.
http://files.engineering.com/getfile.aspx?folder=735fbfe2-3d34-4001-b8d7-b6fc1fceef79&file=Pilz_magnetic_force_safety_switch.pdf

This will alow you to put 1-pole UL 508 20 Amp circuit breaker Altech P/N 1G20UM inside on the panel. This device can be lock out in open position. This I believe would satisfy your UL 508 concerns.
http://files.engineering.com/getfile.aspx?folder=313473c1-2eb3-4cb0-81a0-f0e7314b99e5&file=1G20UM.pdf

Check out the attached literature.

 

David Baird

Sr Controls Designer
EET degree.
Journeyman Electrician.

RE: UL 508A Disconnect

(OP)
Thanks allot for the feed back!  I will investigate this style

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources