Why are generators rated in kW and transformers in kVA
Why are generators rated in kW and transformers in kVA
(OP)
I have a general idea of why generators are rated in kW and transformers are rated in kVA but I am having a hard time truly understanding it. I figured since you dont know what load the generator is driving you would rate in kVA?






RE: Why are generators rated in kW and transformers in kVA
A generator is converting mechanical energy from the prime mover to electrical energy. The engine, turbine, windmill, waterwheel, or kid on a bicycle spins the generator is rated in horsepower = kW. The generator cannot produce any more kw than is supplied by the prime mover. That given, specifying its size in kW makes sense.
A transformer can handle its rated kVA at any power factor. A 100 kVA generator, rated at 0.8 pf = 80 kW cannot supply more than 80 kW. A 100 kva transformer can deliver 100 kw at 1.0 power factor.
RE: Why are generators rated in kW and transformers in kVA
RE: Why are generators rated in kW and transformers in kVA
Where for transformers the KVA rating is at a voltage, marking the heat disapation capability of the tramsformer.
RE: Why are generators rated in kW and transformers in kVA
The transformer is only a pressure (voltage) changer and does not care whether power passing through itself is reactive or resistive or its combination. Its ability is limited only by amperes it can pass through at a given voltage, hence only kVA rating matters. Most kW it can pass thorough would be equal to its kVA rating at unity power factor.
Rafiq Bulsara
http://www.srengineersct.com
RE: Why are generators rated in kW and transformers in kVA
A generator rated at 200 Volts or 208 Volts will have a higher KVA rating if it is dialed up to 240 Volts.
The kW rating of a generator is mos often 80% of the KVA rating and is an indication of the minimum power capacity of the prime mover. It starts to get complicated when comparing standby ratings with prime ratings and different available voltage setings.
But, bottom line, KVA describes the generator end. kW describes the minimum power of the prime mover.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Why are generators rated in kW and transformers in kVA
...or maybe even the maximum :)
RE: Why are generators rated in kW and transformers in kVA
Why not? at unity it should supply 100KW no?
RE: Why are generators rated in kW and transformers in kVA
Only if the prime mover is rated for 100kW plus losses, which usually is not the case.
Rafiq Bulsara
http://www.srengineersct.com
RE: Why are generators rated in kW and transformers in kVA
The untimate capacity of the generator is the capacity of the prime mover, or heat disapation ability, which ever is lower.
At the same time below the rating power factor, full kva can not be achieved because of the excitation limits.
RE: Why are generators rated in kW and transformers in kVA
For instance with just a change in model number the same physical gen-set may be rated at 80KVA/100kW prime power, or 90KVA/110kW standby power.
If that set is rated at 240 Volts, the same set will be rated at 85KVA/70kW at 208 Volts. The dead-rack setting may be trimmed back to 70kW or it may be left at the 80kW. If this is a prime rated set, it will then be capable of outputting 88kW, despite the rating of 85KVA/70kW.
Then we come to excitation. Basic AVR, PMG, load current boost module, saturable PT/CT excitation. These are all rated at 0.8 PF and the capability curves will all be different.
I have probably answered sibeen's comment to some extent.
I have encountered a couple of sets where this was true. Usually there is a little extra capacity in the prime mover to allow for changing atmospheric conditions and engine aging. In Canada a diesel engine may produce 10% more power on summer fuel than it does on winter fuel.
In some installations, for many years old crankcase oil was disposed of in the fuel supply. This increased the SG and as a result improved the power and fuel economy of the prime mover.
With the new generation engines, the fuel filters are much finer to adequately protect the new generation injectors with a much finer spray. With these the cost of replacing fuel filters is greater than the saving in fuel cost.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Why are generators rated in kW and transformers in kVA
Agreed, but that is a prime mover restriction not a generator restriction. We should be careful not to give the impression that a 100KVA generator cannot supply 100KW under any circumstances
RE: Why are generators rated in kW and transformers in kVA
Gt and Rafiq, you may both be correct.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Why are generators rated in kW and transformers in kVA
Rafiq Bulsara
http://www.srengineersct.com
RE: Why are generators rated in kW and transformers in kVA
brian1334:
Objection!
Generators and transformers are always rated in kVA. Just have a look at name plates.
Regards
Wolf
WWW.HYDROPOWER-CONSULT.COM
RE: Why are generators rated in kW and transformers in kVA
Exceed the real kW rating,(which may be greater than the nameplate rating) and you may stall the prime mover and drop the frequency.
Severe overloads on diesel sets often exceed both the KVA and the kW limits.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Why are generators rated in kW and transformers in kVA
You are perhaps more familiar with the large alternators for hydro units, which can almost have endless prime mover power behind it and there just the KVA rating makes sense.
For the rest of us mortals (industrial and commercial applications), a generator is a generator-engine set. Those units are invariably labeled with both kW and kVA rating. Where the engines are picked based on kW rating (as small as possible) and the alternators are typically rated 0.8 pf of that kW rating. In other words, there is no guarantee that the engine behind those alternators can provide kW more than 80% of the alternator KVA rating.
Rafiq Bulsara
http://www.srengineersct.com
RE: Why are generators rated in kW and transformers in kVA
Hi Bill, hi Rafiq:
Yes, you are right, I'm not familiar with generator-sets. As both of you pointed out convincingly, exceeding the kW rating can be a problem or even catastrophic for the prime mover, even if the kVA generator output is within its thermal limits.
As you can see, despite my experience and age, I'm still in the learning curve. Thanks for the comments.
Regards
Wolf
WWW.HYDROPOWER-CONSULT.COM
RE: Why are generators rated in kW and transformers in kVA
Rated in new condition, at sea level, at 20 degree C?
Then it would make since for them to have a derating factor outside those conditions.
It also makes since that a manufacturer would put the smallest rated prime mover as possible to reduce cost.
RE: Why are generators rated in kW and transformers in kVA
Muthu
www.edison.co.in
RE: Why are generators rated in kW and transformers in kVA
Consider an alternator that may safely handle 100 amps.
At 250 Volts that's 250 KVA.
Now we are going to add an engine, but what size?
Standby power;
Normally a 200 kW engine will be used for a PF of 0.8
Prime power;
This rating often allows 10% overload for one hour in 12.
First the gen-set may be re-plated with a nameplate showing the capacity as 227 KVA (May be rounded off to 225 KVA or 230 KVA).
Note, to make it more confusing, there may be one nameplate for the generator and a second nameplate for the total gen-set.
The prime mover will be 80% of 250 KVA, not 80% of 227 to provide enough power for the allowed overload.
So, same engine for the 225 KVA prime power set as for the 250 KVA standby set.
This may be the same physical set with only the nameplates changed or the standby set may have added accessories such as an oil cooler, and/or a larger oil sump.
Then if a lot of run time hours are anticipated, some consultants may spec an engine that it 25% oversize on the theory that there will not be a loss of set capacity should winter diesel fuel be used and the set may run more hours before a rebuild is done on the engine.
Continuous power, it depends, but multi generator N+1 installations are often best described as continuous duty applications.
Then the same set may be rerated for use at 208 Volts. Smoe sets will have a nameplate showing the ratings at all normal voltages for which the set will be used. Some use the nameplate that matches the Voltage that the set was ordered for. As the Voltage drops (for example from 240 Volts to 208 Volts) the KVA drops and the rated kW drops but the actual available kW often stays the same.
One size DOES NOT fit all!
Bill
--------------------
"Why not the best?"