We have a hydrogen cooler for a large electric generator, which requires 2000 GPM of cooling water at 85F. I know the heat load. Evaluating cooler performance with new coolant properties an new coolant temperatures, I need to know the Hydrogen inlet/outlet temperatures.
Does anyone know the typical Hydrogen temperatures for large (300 - 600 Megawatt) pressurized hydrogen cooled machines. Have the temperatures become fairly standardized over the years (like so many parameters for well evolved machines) or are they all over the place.
I am not able to find this data on this 450 MVA machine manufactured in Japan.
Thanks in advance for any help
Does anyone know the typical Hydrogen temperatures for large (300 - 600 Megawatt) pressurized hydrogen cooled machines. Have the temperatures become fairly standardized over the years (like so many parameters for well evolved machines) or are they all over the place.
I am not able to find this data on this 450 MVA machine manufactured in Japan.
Thanks in advance for any help






RE: Hydrogen Temperatures inside Generator
For 750MVA generator with casing pressure of 4Bar and load at 650MW generators cold gas temperaures are normally around 38 to 40 deg.cel and hot gas between 67 to 70deg.cel, this figures are my operational experiences, might differ from plant to plant.
Cooler inlet gas temp alarm is set at 85deg.cel and trip at 90deg.cel. For cooler outlet, alarm is normally set at 45deg.cel. On our machines, the cold gas temps is controlled by auxiliary cooling water control valve which is set at 40deg.cel average of all 4 h2 coolers.
Hope this helps.