I would like to inquire as to what X/R ratio medium voltage circuit breakers are generally tested to sustain their S.C. ratings.

Appreciate any help. Thank you.

RE: Breaker Test X/R Ratio

It's not that simple for ANSI breakers.  For peak current, ANSI allows use of 2.7 times symmetrical fault current.  For close and latch rating they allow 1.6 times.  For interrupting ratings, there are additional factors that must be taken into account.

In addition, the symmetrical current must be calculated per ANSI standards when evaluating adequacy of breaker ratings versus actual duty.

For IEC, it's even worse looking around

RE: Breaker Test X/R Ratio

nightfox1925,

Per ANSIC37 or IEC 60271 (now both are harmonised) all general purpose (not used for capacitor switching) MV/ HV circuit breakers are tested for X/R=17 at 60 Hz (X/R=14 at 50 Hz)

If the calculated X/R ratio is greater than 17 at 60 Hz, like at generating stations, then the manufacturer has to be consulted to purchase CBs tested for a higher X/R ratio so that TRV are with in given limits in both ANSIC37/ IEC 60271.

RE: Breaker Test X/R Ratio

Kiribanda,

I think that is a great oversimplification of the ANSI C37 standards for MV breaker ratings.  But I don't have time to do the research now.  Low voltage power circuit breakers are rated this way, but I do not believe it is that simple for medium-voltage breakers.

I'd recommend referring to Conrad St. Pierre's book on Short Circuit calculations for a comparison of ANSI and IEC standards.  If the medium voltage breaker standards are harmonized, it's news to me and must be recent.   

Cheers,

Dave
 

RE: Breaker Test X/R Ratio

(OP)
Good news guys. I got hold of the switchgear datasheet and it is indicated that:

Symmterical Current = 40kA
Close and Latch Current = 108kA (64kA) Peak

There goes 40 x 1.6 = 64kA, 40 x 2.7 = 108kA

It seems that the breaker is sized as per IEEE Std C37.010-1999 (on a Symmetrical Current Basis).  

RE: Breaker Test X/R Ratio

Yes, but the symmetrical rating is based on certain assumptions that may not apply in all cases.  If the maximum fault current is less than 80% of the interrupting rating, you are probably OK.  If it is closer than that, ANSI C37 methods must be used.

Electrical analysis software packages such as EasyPower and SKM can do this ANSI duty calculation automatically.   

RE: Breaker Test X/R Ratio

(OP)
Thanks dpc, I will take note of that.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources