(OP)
I am working on a project in Rochester, NY and want to utilize an above ground heated enclosure (Safe-T-Cover) to house an 8" water meter. The enclosure is to be slab mounted. I'm wondering if the heat produced within the enclosure (from a slab mounted heater) will be sufficient to prevent the slab from heaving. Should i consider having the slab foundation bearing below frost line to prevent damage to the watermain that will be projecting through the slab? Any thoughts are appreciated.

RE: Above ground water meter enclosure

Yes.

RE: Above ground water meter enclosure

If enclosure is maintained above 40 degrees or so it should be possible to protect it and and ground below from freezing. I'd suggest designing the slab like a frost-protected shallow foundation.  Thicken the edge 12"-18", put vertical subgrade insulation around it, and maybe some horiz insulation also.
Use some flexible material around the pipe to allow a little slab movement without stressing the pipe, similar to a concrete expansion joint.  Or a modular/flexible insert designed for this purpose.

Hydrants are installed in cold climates through sidewalks without any special precautions, other than some clean fill under the sidewalk.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources