Parallel Conductors

Parallel Conductors

Parallel Conductors

(OP)
Are parallel conductors smaller than 1/0 awg in conduit allowed under the Canadian Electric Code?

RE: Parallel Conductors

With restrictions. Smaller conductors in the same cable may be paralleled to reduce voltage drop IF the breaker will adequately protect any single conductor.
EG, Any number of 15 amp rated conductors (#14AWG) may be connected in parallel IF they are contained in one cable they are fed from a 15 amp breaker.
You may run a multi conductor cable in conduit to comply with this rule.
In the 2006 code this is rule #12-108(3).
Neutral conductors less than #1/0 AWG may be run in parallel under certain conditions, see rule 12-108(4)

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Parallel Conductors

(OP)
Thanks, Bill
So running 2 #1 awg per phase to supply a 125 HP motor would not be allow?

RE: Parallel Conductors

Just because im curious, why would you run parallel #1 cables? You're only going to get about 250A out of the deal? Plus is the motor lugs set-up for parrallel runs? You cant shove two wires into one lug and clamp it down.. Plus where are you going to find a breaker that small with duel lugs? Is is a bend radis issue or something?

RE: Parallel Conductors

(OP)
jwparker, I am reviewing a design by a Canadian vendor for installation in the US and trying to determine if they were following Canadian standards.  The engineer followed the vendor's design but we caught it in time and installed 1-3/0 per phase.
Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources