Is NFPA #13 8.15.1.2.9 referencing a DIFFERENT type of small room?
Is NFPA #13 8.15.1.2.9 referencing a DIFFERENT type of small room?
(OP)
NFPA #13 2007 Ed.
8.15.1.2.9 Concealed spaces over isolated small rooms not exceeding 55 ft2 (5.1 m2) in area shall not require sprinkler protection.
"Isolated small rooms" is this meant to be a reference to the definition of a "small room" as indicated in 3.3.15 meaning it has to be light hazard etc.?
Also, does "isolated" refer to being remote or to being separated from other adjacent rooms with a fire rating?
8.15.1.2.9 Concealed spaces over isolated small rooms not exceeding 55 ft2 (5.1 m2) in area shall not require sprinkler protection.
"Isolated small rooms" is this meant to be a reference to the definition of a "small room" as indicated in 3.3.15 meaning it has to be light hazard etc.?
Also, does "isolated" refer to being remote or to being separated from other adjacent rooms with a fire rating?





RE: Is NFPA #13 8.15.1.2.9 referencing a DIFFERENT type of small room?
do not have the book, but do not believe any rating is required, maybe fire blocking only?? think the idea is fire maybe will not start there, or no reason to require spinklers in the area
if you think of an area above a ceiling in a restroom, something like that small
RE: Is NFPA #13 8.15.1.2.9 referencing a DIFFERENT type of small room?