PT100 VS TC
PT100 VS TC
(OP)
Dear friends,
If I want to measure the signal from PT100 and PT50 sensors, how is the measuring unit? It will be measured by Calibrator.
And for thermal couple? Is its signal in Volt?
Regards,
HienN
If I want to measure the signal from PT100 and PT50 sensors, how is the measuring unit? It will be measured by Calibrator.
And for thermal couple? Is its signal in Volt?
Regards,
HienN





RE: PT100 VS TC
A TC should measure volts. Way less than 1Volt. Millivolts.
If you grab it with your fingers, the value should raise or drop, depending on the polarity you've hooked up with your Digital Volt Meter(DVM).
Keith Cress
kcress - http://www.flaminsystems.com
RE: PT100 VS TC
If you measure with a calibrator as you've stated, you can measure in whatever unit you want (F,C, ohms for RTDs and F, C, mV for TC). You just have to tell the calibrator what you are measuring and what Unit you want.