I am trying to calculate the size of inductors for a three phase shunt reactor bank to provide 3MVAR at 33kV.

Calculations
XL=(kV^2)/MVAR = 33^2/3 = 363 ohms

L= XL/(2piF)= 363/376.99 = 0.962 Henries

Is this value correct, if so will the bank require an indcutor of 0.962 henries per phase?
This is where I get a little confused.  Will three 0.962 Henry reactors (one per phase) form a 0.962 reactor bank?

I know that with capacitor banks a 600 kVar bank is formed of 3- 200kVar units.  200 kVar per phase.   

RE: Shunt Reactor Bank calculations

(OP)
I just realized my last question does not make much sense..
what I meant to ask was if three inductors of 0.9 henries (one per phase) will give me a 3MVAR bank at 33kV? based on shown calculations.

Thanks

RE: Shunt Reactor Bank calculations

Hint: You need to use per phase voltage and per phase MVAR to calculate per phase XL

Rafiq Bulsara
http://www.srengineersct.com

RE: Shunt Reactor Bank calculations

anteg,

What you've done is correct.  You can use either
3-phase MVA and kV ph-ph

or

1-phase MVA and kV ph-n

Both will give you the same result.

RE: Shunt Reactor Bank calculations

Agreed.  Using single phase values will remove his confusion, though.

Rafiq Bulsara
http://www.srengineersct.com

RE: Shunt Reactor Bank calculations

Why do you think you need reactors? I have installed caps on a 34.5 kv line and used fused cutouts.

RE: Shunt Reactor Bank calculations

I think it's good for you to understand the calculations.

However, you can simply tell your reactor supplier the voltage and MVAr you need and they'll take it from there.

 

RE: Shunt Reactor Bank calculations

(OP)
Scottf,

It is true that I can just let someone else handle this, but I would like to understand what needs to be done before we move forward with a project.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources