13.2kV & 480V Conduit Separation

13.2kV & 480V Conduit Separation

13.2kV & 480V Conduit Separation

(OP)
Is there any reason (safety, technical, or otherwise) that 13.2 kV and 480V conduits cannot be run on the same conduit rack?

If so, what should be the minimum separation between conduits of these two voltages?

Thanks!
Mike

RE: 13.2kV & 480V Conduit Separation

Both can be run on the same rack and there is no required separation distance between conduits per NEC, that I am aware of.

I would segregate the high voltage conduits away from the low voltage conduits to the extent possible, just for increasing awareness of high voltage circuits.  

RE: 13.2kV & 480V Conduit Separation

What is a rack?

Regards,

Lyledunn

RE: 13.2kV & 480V Conduit Separation

You can pretty much do whatever you want with your conduits, there's no requirement for separation.  As a matter of practicality, though, you'll probably need about 2" minimum betwen them to get a wrench in to the connectors.

RE: 13.2kV & 480V Conduit Separation

Although there is not a Code requirement per se, there is hidden in the National Electrical Code (in the NEC Handbook commentary for article "310-15    Ampacities.") some sage advice.

In sum and substance, the advice is to maintain conduit Center to Center spacing as would be used in laying out conduits for entry into a junction box. "...Field experience has indicated this degree of spacing between runs has not caused any problems....". 1996 NEC Copyright 1995 NFPA.

This is consistent with the empirical nature of the ampacities cited in the code.

RE: 13.2kV & 480V Conduit Separation

It can be run on the same rack for power conduit but if possible try to provide space between them.There were some effect on the excitation but it will cancell each others. Normally the separation is require when involved with instrumentation system which using DC voltage or mA signal.

RE: 13.2kV & 480V Conduit Separation

Suggestions: The following needs to be noticed:
1. Industry practices, e.g. nuclear, non-nuclear
2. Grounding practices, IEEE Stds 80, 142, etc.
3. Type of conduits
4. Etc.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources