more - Minimum Concrete Cover Tolerance

more - Minimum Concrete Cover Tolerance

more - Minimum Concrete Cover Tolerance

(OP)
Am inspecting on a job where the elevated slabs are 3' thick with #6@6 bot. short-way, #6@12 bot. long-way, #6@12 top long-way and #8@6 top short-way.

top mat cover reqd. = 3/4"

With the tolerance in reduction in cover can be 1/2".

In the completed slabs, LOTS surface cracks in the short-way direction, spaced curiously at multiples of 6".

Is the full 3/4" of concrete cover enough to provide sufficient aggregate interlock over that big of a bar to prevent these cracks?  Or am I just barking up the wrong tree altogether?    

RE: more - Minimum Concrete Cover Tolerance

Did you take a look at the concrete mix design?  Often when there is not a lot of cover, a mix with smaller aggregate will be used.  This is the first place I would look.  

RE: more - Minimum Concrete Cover Tolerance

DWHA is correct about looking at the mix design.  For a 3/4" cover on the slab, the maximum size of the aggregate would be about 3/16"....that's pretty small for concrete aggregate.  You could also interpret the code to mean the aggregate in this application should be no more than 1/2".  In either case, you have to look at the mix design to check the nominal coarse aggregate size.

If the mix design was for No. 57 stone, with 3/4" cover, that could cause aggregate segregation and the cracking you noted.

RE: more - Minimum Concrete Cover Tolerance

I think what you are seeing is plastic settlement cracking.  In a thick slab, revibration is required if these cracks over the bars are to be prevented.  This type cracking can occur even with much larger cover if the consolidation is inadequate.  Often seen in the top of footings which have top bars.

RE: more - Minimum Concrete Cover Tolerance

Settlement cracking is likely the correct explanation, but 3/4" cover is not enough for a 36" thick slab.  It should be at least 1.25" in my opinion.

BA

RE: more - Minimum Concrete Cover Tolerance

(OP)
It's a #7 stone mix and the cover was increased to 2".

Possible formwork issue?

RE: more - Minimum Concrete Cover Tolerance

I doubt that it is formwork related.  If the cracks follow the #8 top bars, it is almost certainly plastic settlement cracking due to inadequate consolidation.  Another possibility would be restraint shrinkage cracks, but as you said there are LOTS of cracks, that doesn't sound like planar shrinkage.  No cracks on the bottom surface?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources