Generator bearing resistance

Generator bearing resistance

Generator bearing resistance

(OP)
Hello,
we are about to specify a 6,25MW 6-pole induction generator for a DFIG drive system. I know that shaft voltages and resulting bearing failures have been a great deal sometimes. Also I know that effective shaft grounding at both drive ends helps, but how shall the bearing insulation be done? Is it suffficient to state e.g. a 10MOhm bearing resistance, shall both bearings be insulated or better just one?

Who has experience or can probably recommend any expert in this field?

Thanks for any input and regards, Pat

RE: Generator bearing resistance

At that size, I assume it's white-metal bearings. The question is whether they are mounted on the generator frame or they are supported independently on separate bearing pedestals.

In the former case, the bearing manufacturer would insulate the bearing housing (normally Teflon coated) so that bearing is isolated.

In the latter case, an fiber glass insulation pad of about 10 mm thick is placed beneath the pedestals and the fixing bolts are insulated along with fiber glass washers. Also, any external oil lines have to be isolated from the bearing reservoir to by way of insulated bolts and washers.

A 10 Megohm resistance is ample for such insulation.

As for insulating one end or bot ends, hopefully Gunnar (Skosgurra) would chip in since he is deeply involved in EDM in bearings.

RE: Generator bearing resistance

(OP)
Dear edison123,
thanks a lot for the information. The bearings are integrated inside the generator case (no pedestals). My feeling is that insulating both bearings is the method of choice: If you let one bearing be conductive you'll never know if a current loop could build with shaft external equipment (coupling, GBX or slip ring unit, encoder etc.). However I can not backup this view with facts.

Best regards, Pat

RE: Generator bearing resistance

What is effective shaft grounding?  
We have used carbon brushes and slip rings on VFD motor shafts with limited success.  I suspect that the problem here is that the carbon brush will not conduct until there is a 0.5 volt differential accross the brush and the slip ring, but the grease in the bearing will start to conduct at 0.3 volts.  I don't have facts and data to support these assumptions.

 

RE: Generator bearing resistance

The manufacturer should have published data on the minimum bearing insulation resistance.  

RE: Generator bearing resistance

Hi Pat

I have seen ABB motors with frame mounted sleeve bearings with both side bearings insulated. They were ring-oil lubricated with no external oil supply. They also had a grounding brush at the coupling end.

I think Gunnar is enjoying his holidays and hopefully he will chip in soon.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources