Using a 351 relay for LTC control
Using a 351 relay for LTC control
(OP)
Someone here has proposed using a SEL-351 relay to also do LTC control. I'm sure it can be done, although I haven't seen any papers on it yet.
Has anyone done this, and if so what problems did you encounter?
Has any one seen any papers on this?
Has anyone done this, and if so what problems did you encounter?
Has any one seen any papers on this?






RE: Using a 351 relay for LTC control
and undervoltage to raise it
if you don't need load compensation and parrallele stuff that could be easy
RE: Using a 351 relay for LTC control
At first glance this looks to easy. So what am I missing?
RE: Using a 351 relay for LTC control
It should be easy. Just make sure the timers are set up to keep from accidentally chattering the outputs.
Also, make sure you don't have latches or SER points that chatter. Each time they toggle, the position is written to the non-volatile memory. The EEPROM has a finite number of writes (about half a million), and you don't want to max it out.