PT protective fuse rating

PT protective fuse rating

PT protective fuse rating

(OP)
I have to connect outdoor type 600VA, 33kV/220v PT thru protective fuses at the primary to 33 kV (line to line) . The supplier has provided 24kV, Siba make outdoor type  , e=442mm ,Ia= 40kA  fuses, is it Suitable ?. Please guide me.

RE: PT protective fuse rating

If the 33kV system is effectively grounded and the PTs are all connected line-ground on the 33kV side then the 24kV fuses should be sufficient.

RE: PT protective fuse rating

(OP)
PT is connected between Line to Line of 33 kV System.

RE: PT protective fuse rating

Then you must have 33kV fuses. But line-ground is a far better connection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources