Asbury loop
(OP)
Can anyone tell me where to find information on the Asbury loop. I am a lineman at Pacific Power and some on my co-workers are telling me it is best way to ground a single phase transformer. I disagree and also it is not our construction standard.
Thanks Zach
Thanks Zach






RE: Asbury loop
Maybe someone here will know:
http://www.line-man.com
Mike Halloran
Pembroke Pines, FL, USA
RE: Asbury loop
ht
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Asbury loop
Asbury is an adjective,
and Fargo is a verb.
.. and we lack the correct dictionary.
Or
The leader from the note that references note 6 appears to be pointing to the corrugated duct, not the ground wire, as if it were asking the contractor to wrap the wire around the duct in some specific way, known as a 'Fargo to Asbury Loop'.
Or
The drawing was produced by a professional drafter like my friend Ralph, and not back-checked by the engineer who did the original sketch. I.e., the drafter couldn't read the chicken-scratches.
(Ralph was amazing; you could give him a pile of sketches on cocktail napkins and get back a beautiful E drawing in an afternoon. He was like a machine. Also as smart; your sketches had to be correct.)
Mike Halloran
Pembroke Pines, FL, USA
RE: Asbury loop
Mike, that is too funny. see my post here:
http:
RE: Asbury loop
I agree with you about good draftsmen being amazing. That work can truly be an art form. Pen & ink used to separate the men from the boys.
RE: Asbury loop
RE: Asbury loop
I think someone at your place of employment is yanking your chain. The diagram you show is for a two-bushing transformer. With the two-bushing transformer, the H2 bushing could be connected the one of the primary phases or the primary neutral depending on the system voltage and transformer voltage.
With a single-bushing transformer, H2 is connected to the primary neutral. The primary and secondary neutral are bonded. X2 is connected to the secondary neutral. The secondary and primary neutral are bonded and that is essentially how you get the H2 to X2 tie.
You would have the same H2-X2 tie if the H2 of a two-bushing transformer were connected to the neutral.
But I don't think that has anything to do with the original diagram you posted.
As I said in the post I linked, "Asbury" must be a typo. It probably started out as a dictation of "as-buried" or some such reference. Fargo is a brand of connector and would mean to use a compression connector on the wire.
RE: Asbury loop
RE: Asbury loop
I might buy into one of the primary loops being called the "Asbury loop" due to location. Also, you might want to clamp the ground wire to the concentric neutral.
The problem is that is makes no sense to name and isolate one primary as such. If you would bond one, you would bond any.
Some amorphous dedicated ground loop running from "Asbury" to "Fargo" is not likely either. Besides, you would not just loop the ground loop into a loop.:)
It is just a typo. Don't read so much into it.