50Hz Transformer run on 60Hz system
Good afternoon all,
I am modeling a system that appears to have 50Hz equipment running on a 60Hz system.
I am particularly interested in knowing the affects of this difference in frequency on nameplate ratings on transformers. I can guess that the %Z would be 120% of the listed %Z due to the frequency increase, but I feel there are other considerations that I am overlooking. Are there any notable references (or threads in this forum -- I was unable to find what I was looking for) on this subject?
Thank you for the help,
Tim
RE: 50Hz Transformer run on 60Hz system
Re %impedance. The  impedance is the vector sum of the resistance and the reactive inductance. resistance is not frequency dependent, inductive reactance is frequency dependent. The X/R ratio will change.
Bill
"Why not the best?"
Jimmy Carter
I read the motor FAQ and bookmarked it (great article!)
One question from that FAQ: it states that cooling is reduced when a 60Hz motor is ran at 50Hz. What is physically occurring that would cause the cooling to be poorer when run at 50Hz... is it due to the higher V/f ratio?
Thanks for the help,
Tim
The motor is running at 5/6 normal speed, so the shaft mounted cooling fans are not providing normal air flow.