Development Length
Development Length
Folks,
I have a question that may come across as retarded, but I gotta ask.
A standard hook for a #4 bar is 12 db = 12*0.5=6".
What happens for a #4 U bar or a #4 stirrup? Is the requirement that you need 2 * standard hook = 24 db to develop the bar?
RE: Development Length
DaveAtkins
See ACI 7.1.
I guess I did not express myself correctly.
A quick sketch:
|____|
What is the minimum length (based on db) of the horizontal leg of the U to develop this stirrup?
2" + 2(1/2" bar dia) = 3" total width.
Another question I have is this:
How much concrete should you have around a reinforcing bar in order to adequately transfer the stresses from reinforcing bar into concrete?
Assuming that you have a #5 bar, what is the minimum cylindrical area around the bar needed so that it does not pull out (precluding tension failure in concrete).
The australian code requires an increase in the development length of around 25% when there is more than 300mm of concrete below a bar (to allow for a void formed under the bar due to the slumping and shrinkage away from the bar of the concrete mass under)
I would assume the minimum cylindrical area is the minimum development length required by your code multiplied by the circumference of your bar
Assuming that you have a #5 bar, what is the minimum cylindrical area of concrete around the bar needed so that it does not pull out.
Read Chapter 12 of ACI. It explains the logic well.
The formula for development is based on the cover/spacing to the bar and the bar diameter. It is not expressed in terms of a cylinder of concrete required.