Transformer and Thermostat Operation at - 40Deg C

Transformer and Thermostat Operation at - 40Deg C

Transformer and Thermostat Operation at - 40Deg C

(OP)
I have a heat trace controller used for heating insulated busbars for an overhead crane installed outdoors.

The minimum ambient temperature during winter time here is -40 Deg C.

The controller box has a Thermostat controller rated for

-34 to +66 Deg. C (Operating)
-40 to 85 Deg C (Shipping)

A 250VA dry type CPT and Square D magnetic contactor are also installed in the same control box (NEMA 4X).

I am intending to install this heater control box outdoors near the busbars to be heated. The control box components will be subjected to -40 deg C.

I would like to get some guidance if this will be acceptable. Furthermore, I am not sure on the "shipping" temp. ranges for the thermostat mean.

I will appreciate any comments. Thank you.
 

RE: Transformer and Thermostat Operation at - 40Deg C

It means the device will survive in the box at -40 deg C, but is not meant to be operated at -40 deg C.
   

RE: Transformer and Thermostat Operation at - 40Deg C

An anecdote that may or may not be important.
We had a temperature alarm that had a limit of about 32F. We wanted to use it outdoors in a colder ambient. We did some testing and found out that the operating limit was the limit of the thermocouple reference junction correction. As the temperature went lower, the alarm point went lower by the same amount. That is at -10F the device alarmed 10F below the set point. We decided that if we were getting close to alarm conditions when the ambient was that low, we didn't mind the alarm coming in a little early. We used the device as is and never had a problem.
We had a similar problem with hoar frost forming on overhead crane bus bars. We installed a power correction capacitor at each end of the bus bars (center fed) and the current to the capacitors was just enough to keep the hoar frost off the bars.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources