KEB Combivert Drive

KEB Combivert Drive

KEB Combivert Drive

(OP)
We have a KEB Combivert Drive, F5 series Ruvatronic RT5/1001 driving a Leybold Roots vacuum pump. The X2a control card is wired to run the drive at a fixed speed of 50 hertz but for some reason the drive would not go above 10 hertz. I am told they had this problem before and swapped out the drive and it fixed the problem. KEB says they cannot supply a replacement for 5 weeks and this is a critical piece of machinery. It was sent out for repair. I was unable to check the system out or do any testing beforehand. They tell me the drive was not faulted or displaying any errors so I am concerned the problem is likely not the drive but I do not know the system well and I am not very familiar with KEB drives. Tech support was not much help. I know it's not much to go on and I apologize for that but just throwing it out there in case someone is familiar with this system and could point me in the right direction. Any comments or advice\help would be greatly appreciated.   

RE: KEB Combivert Drive

Check the current limit setting.
Check that the unused inputs are clear.
Check the motor parameter settings.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: KEB Combivert Drive

(OP)
Thanks Bill, Checking the parameter setting for constant current setting it states " if this value is exceeded it will reduce the output hertz till it is in range again" (paraphrasing). I believe the issue is mechanical and this is what is happening. When I get it back I will install the drive and monitor this parameter. It gives a indication if it is in a stalled state.

RE: KEB Combivert Drive

Check against the other drives. It may be set too low.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: KEB Combivert Drive

It could be something as basic as the fixed frequency setting not being 50Hz.
Maybe try another method of running the VFD-use the keypad and run up to 50Hz from there or use a 0-10Vdc input/potentiometer to get to 50Hz.
However, if it is a critical piece of equipment and the turnaround is 5 weeks, I would be looking at another supplier for my VFD.
 

RE: KEB Combivert Drive

Your best source of information for this system should come from Leybold.  

This is a proprietary system out of Europe.  They have been using the KEB Combiverts for many years and have had special firmware designed for their application.  Not a standard off the self VFD and I am sure that the new inverter would be coming from Europe.

This is the first Leybold system that I have heard of using the KEB F5 generation of inverters.  Do you have a part number of this inverter (ART-NR)?

Are you getting any errors on the inverter itself?

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources