DC motor testing

DC motor testing

DC motor testing

(OP)
Question!! I got a DC motor that has quit on me ....I meggered it ...

+ to G  is 430M ohms
- to G is 2M ohms
+ to - is 350M ohms

doesn't seems right to me, am I doing it wrong ??? is there a difference on testing AC and DC motors??
 

RE: DC motor testing

You sure about those numbers? What are the motor ratings? What voltage did you test at? What was your PI? What was winding temp at time of test?

RE: DC motor testing

looks like an open winding

RE: DC motor testing

(OP)
Motor infor:

1/4 HP
12VDC
2600RPM
Tested at 250V
I did not do the PI,
the testing enviorment temperture I would say it was about 95 degree F

RE: DC motor testing

Perhaps the brushes are worn out?

RE: DC motor testing

350 MegOhms from + to - looks like an open. Second to roydm, check the brushes.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources